  1. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,991
    Location:
    Vero Beach
    The best question has been asked. Does the problem persist when under generator power? Eliminate voltage as a variable.
  2. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,950
    Location:
    Miami, FL
    Cruisair chillers start up with amps ramping up slowly and smoothly. No jump no peak. I ve set up the main page of our monitoring system to include bar graphs for amps pulled and I can see when either start by the slow increase (over a couple of seconds). That’s the whole point of VFDs
  3. captholli

    captholli Senior Member

    Joined:
    Jan 4, 2010
    Messages:
    1,214
    Location:
    In The Bilge
    Exactly, VFD's simultaneously ramp voltage and Hz. up slowly as to alleviate hard start current in-rush. Scroll compressors start with unloader valves open and make even less initial load with VFD's.
  4. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,991
    Location:
    Vero Beach
    Agreed. The Technicold units spin up gently, and I can watch my amperage draw dial up with them. There is no spike. There is no old fashioned start load jump.
  5. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca
    Of course no dips or errors in voltage for last 3 days. We are running a light ship with no water heater or freezer, etc. so 100a is fine.

    It would be cool if you could record the dip in voltage at the pedestal with some kind of recorder.
  6. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,950
    Location:
    Miami, FL
    If you have monitoring system like we do you can adjust the low voltage alarms to record when it happens.

    Otherwise increase amps by adding loads to see if you can duplicate the error
  7. captholli

    captholli Senior Member

    Joined:
    Jan 4, 2010
    Messages:
    1,214
    Location:
    In The Bilge
    Fluke and Tripp make a voltage data logger scope that you can clip the leads to your L-1 & L-2 buss and it will record voltage and amperage up to 72 hours. Of course these loggers are relatively expensive and wouldn't belong in a yachts tool box so any good marine electrical outfit will have one to assist you in getting a good 72 hour graph of what's happening.
  8. wdrzal

    wdrzal Senior Member

    Joined:
    Feb 6, 2006
    Messages:
    415
    Location:
    Allegheny Mountains of Western Pa
    Technically if this is the case you have a VVVFD (variable voltage, variable frequency drive). This coupled with a technology Honeywell first patented, VAV/VT (variable air volume /variable temperature), produces the ultimate in comfort ,low noise and efficiency .
  9. bayoubud

    bayoubud Senior Member

    Joined:
    Feb 19, 2017
    Messages:
    1,148
    Location:
    Florida
    A heads up for those that have a Aqua Air Marine AC system, my ac tech said he was told by one of their big S Florida dealers they are closed. We suspected something was wrong, we have been waiting for 6 weeks after ordering a fan unit for one of our air handlers and nobody was answering the phone or responding to emails about shipping.