Click for Ocean Alexander Click for Perko Click for Northern Lights Click for Mulder Click for YF Listing Service

combine 3 phase 125 amp dock power into one 250 amp shore cord?

Discussion in 'Technical Discussion' started by sdowney717, Oct 3, 2024.

You need to be registered and signed in to view this content.
  1. sdowney717

    sdowney717 New Member

    Joined:
    Oct 28, 2016
    Messages:
    11
    Location:
    Poquoson VA
    A guy with a big boat in the Med is at marinas that only have 125A 3 phase power, and his boat has one shore inlet 250A 3 phase power. Can two 125A dock power sources be combined to run the entire boats 250A shore power?

    Like a Y adapter? Or is this never going to work.
  2. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,434
    Location:
    Satsuma, FL
    In theory, yes.
    In practicality, NO.
    Safe, Absolutely not.

    Either split the ships loads on two (seperate) 125A leads or install a power controller like a big Atlas.
    Either way will still require 2 x 125A leads.
  3. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,544
    Location:
    Miami, FL
    A “big boat” with 250 Amp shore power must have some type of shore power system to allow various configuration, doesn’t it ?
  4. sdowney717

    sdowney717 New Member

    Joined:
    Oct 28, 2016
    Messages:
    11
    Location:
    Poquoson VA
  5. sdowney717

    sdowney717 New Member

    Joined:
    Oct 28, 2016
    Messages:
    11
    Location:
    Poquoson VA
    I think that may be what he has at the dock, access to 2 125a power, but his boat is a single 250 amp cord connection

    3 phase 50 hz European power.
  6. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,732
    Location:
    Vero Beach
    The smart Y works for smaller loads because it’s only handling single phase output using opposing phases to balance the increased load. This setup won’t work if phases are inline, and Hubbell rejects the B outlet and won’t stack the amps. I don’t see where that technology can work in a Y setup. Seem logical that it can only be managed by an on-board power system navigating two cords. If you think about it, you’re pulling 125 amps from an outlet wired for 125 amps and no extra leg to share the extra 125. If a Y could do that you’d be pulling 250 through wires intended for 125. That wouldn’t last long……
  7. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,544
    Location:
    Miami, FL
    reverse Ys have circuitry to allow pulling from two receptacles and combining the output. Works pretty well when connecting a single phase 100 amp inlet to two 50 amps outlets. The circuit will only allow the connection if both legs are connected to compatible outlets.
  8. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,732
    Location:
    Vero Beach
    Yes, I have Hubbell's smart Y for the 100 to two fifties. Ive never seen a unit for two 125's. Ive only witnessed vessels using two 3 phase cords and managing loads aboard.

    FWIW, Hubbell's smart Y allows for in phase outlets to serve you with 50 amps alone, whereas Marinco won't function if the outlets are in the same phase.
    BlueNomad likes this.