    Does anyone know what the 120VAC breaker labeled "Ext Outlets" goes to? I'm not aware of any external to the house 120VAC outlets except the one on the bridge, which is on the "Quartz Lights" breaker?

    The back story to asking:

    We have been to numerous marinas with the new spec power pedistals and had no problem until last weekend. We had been at that marina a couple years ago also with no problem. We were able to get a workaround so we could stay. Back at home I went to check the ground to neutral's (I had fixed a problem from PO wiring several years ago). I easily found a new short (fluxuated a lot but as low as 2 ohm and high as 100) between the "A" neutral bus and ground.

    I disconnected neutrals one at a time and tested until the partial short went away. The neutrals are grouped 2-4 to a lug. I left the suspect lug disconnected and connected to shore. Every breaker I turned on and checked, everything worked. The only breakers I can't easily check to see still works are the block heaters (I know which neutral they are on as that is what I fixed several years ago) and the "EXT OUTLETS".

    I expect the EXT OUTLETS is wired but not used so there are dead-head lines somewhere in the boat and over the years one has had the insulation protection fail so there is now a partial short, likely being wet. Problem is I don't know what 'could' be connected to them so don't even know where in the boat to look.

    Thanks
  2. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,391
    Location:
    Satsuma, FL
    I remember a find; outlet boxes under the cockpit comings.
    Greg Page likes this.
  3. Seth Fisher

    Seth Fisher Member

    Joined:
    Sep 9, 2016
    Messages:
    45
    Location:
    RI
    Agreed. Quartz lights were in the engine room from what I recall
    Greg Page likes this.
  4. Greg Page

    Greg Page Senior Member

    Joined:
    Mar 4, 2017
    Messages:
    433
    Location:
    Annapolis MD
    Only wires under the cockpit comings are for the 12 VDC cockpit lights, unless they don't exit the plastic tube and stay in engine room.

    Quartz lights are on the hardtop (aft facing), and a 120VAC outlet box inside the helm console that now runs the Starlink. Engine room lights on ours are on the 12VDC sircuits.

    small IMG_5117.jpg
    Last edited: Sep 30, 2024
  5. ranger58sb

    ranger58sb Senior member

    Joined:
    Aug 20, 2013
    Messages:
    895
    Location:
    Chesapeake Bay, USA
    Completely different boat, builder, etc...

    But FWIW our "external outlets" breaker controls one in the cockpit, one on the bridge, and two in the engine room. I hadn't actually noticed the second one in the engine room 'til just the other day...

    -Chris
    Greg Page likes this.
  6. Greg Page

    Greg Page Senior Member

    Joined:
    Mar 4, 2017
    Messages:
    433
    Location:
    Annapolis MD
    Thanks. There was one in our engine room. Installed by a PO using romex and hooked to the ice maker circuit. I removed it LOL.
  7. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,819
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    Hi,

    Older boat but similar layout.
    In the picture you posted, my boat has a duplex outlet mounted above the power inlet and the power inlet itself is lower on the bulkhead than yours.

    On my rig you can easily remove the inside panels,( they would be forward of your inlet, like blank plates, to gain access to the area behind the inlet) which you don't have because yours is a 43 or 42 and the cockpit is a little smaller, but maybe the deck outlet cable is in coaming or accessible from the engine area.
    I can sort of get to the inlet cable from my engine room but not easily.

    The insulation in the engine room hides a lot of wires in my boat.

    I have a phone/cable TV inlet in the same area, also accessible from the side panels.

    My panel directory has no EXT OUTLETS but calls out the Shelter circuit and the Cabin circuit which are outlets and lights.
    Greg Page likes this.
  8. Greg Page

    Greg Page Senior Member

    Joined:
    Mar 4, 2017
    Messages:
    433
    Location:
    Annapolis MD
    Mine has the phone inlet alongside the power inlet. It used to have two shore power inlets, they were removed and the current 120/240 50A inlet put in it's place. The external shore power goes to two separate (A & B) breakers on the corner post in the interior directly above the outside recepticle. Power runs to two (A & B) dual breakers in the main distribution panel on the back galley wall.

    The ground/neutral problem is past the breakers in the distribution panel, as when the A breaker, load and neutral, is open there was no trip. Also the B breaker and all it's sub circuits worked fine.

    Getting a quote for an isolation transformer, but for now just leaving the unknowa neutral bundle disconnected.
  9. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,819
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    Do you have any 120 volt outlets on the rear deck ?
    Do you have one or two on the bridge ?
  10. Greg Page

    Greg Page Senior Member

    Joined:
    Mar 4, 2017
    Messages:
    433
    Location:
    Annapolis MD
    There are no 120 volt in the cockpit or main deck.
    There is one 120v on the bridge, which is on a "B" circuit and works (runs Starlink).
    There are two 120v in the engine room, on a known breaker, and work (battery chargers).

    I haven't yet found any 120v, lights, appliances, outlets, I've used that isn't working with the suspect neutral(s) removed.
  11. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,819
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    A circuit tracer might help you there.
  12. Greg Page

    Greg Page Senior Member

    Joined:
    Mar 4, 2017
    Messages:
    433
    Location:
    Annapolis MD
    I've never had or used a circuit tracer. How far away can they detect, since all the wiring is behind panels, floors, ceilings? Can they be used on a deadended circuit?
  13. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,819
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    I have one of these
    I've been successful following wires behind drywall in houses and behind headliners and fiberglass on boats.
    This unit will trace live or de-energized circuits
    There are cheaper ones out there but the cheap ones need voltage on the circuit to work which is not better IMO.
    The worst part about it is re-learning how to use it after it sits for a year in it's case.

    https://www.triplett.com/products/3399-fox-hound-premium-tone-inductive-amplifier-probe-kit
    Greg Page likes this.
  14. Greg Page

    Greg Page Senior Member

    Joined:
    Mar 4, 2017
    Messages:
    433
    Location:
    Annapolis MD
    I went back into the panel and the EXT RECPT breaker doesn't have an ouput wire so has never been active on our boat. Finding where the bad neutral goes is an academic issue for now. I will look into the line tracer for another time when I'm up for crawling through the internal spaces following wires. I've been changing my 65 Corvette to a new fuel injection system, removing all the old wiring and installing new ones, and for now my somewhat older body has had enough bend, fold and spindle.

    Thanks
  15. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,819
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    Welcome, good luck.
  16. C team

    C team Senior Member

    Joined:
    Nov 1, 2011
    Messages:
    249
    Location:
    Kent Island
    Greg, I recently run into an issue at a marina with newer pedestal on the West River. I kept tripping the breaker at the dock. I suspect I have to find where I might have a neutral causing the issue. I called a company in Annapolis about doing the work and a month later, still waiting to hear back. Hard to find service for electrical on Kent Island.
  17. Greg Page

    Greg Page Senior Member

    Joined:
    Mar 4, 2017
    Messages:
    433
    Location:
    Annapolis MD
    There are a few things you can check yourself if you have a digital resistance meter.

    Turn off all the 120v main breakers on the panel and remove the shore power cord.

    First check the shore power cord to see if there is a circuit between any of the 'pin' circuts and the ground plate on the side (I'm presuming you have a 120/250 cable) If there is the cable is bad.

    Next go to the panel and turn off all the individual 120v breakers, and the A and B 120v master breakers
    Open the panel and check for a circuit between the A neutral bus and the ground bus, then the B neutral bus and ground
    If there is (like I had this last pass) you can disconnect the individual neutral lines on the bus that had the circuit one at a time until you find the one that has a circuit to the ground bus. Then insulate it, reconnect shore power, and test circuits on that bus one at a time to find which one no longer works.

    If there is no circuit from either bus to ground with all the breakers off, turn on breakers one at a time starting with the bus master and re-test. When you find a circuit between the bus and the ground someting on the circuit just turned on has the problem. (In my earlier case it was the block heater circuit. I opened and checked all the points on that circuit I could access. I found one junction box where the ground and neutral had been crossed.)

    If everything works, then you may have the same unknown issue I have. But if everything works you can go boating.

    -g
    C team likes this.
  18. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,391
    Location:
    Satsuma, FL
    Sadly, if the dock service has the early GFI service breakers, It may take some time and patience to find your Green & White wire issue.
    I usually look at the gen-set G & W strapping first.

    Best fix I can imagine.
    Go boating, Get off the dock
    Dock breakers don't trip when off the dock and slip empty...;)
    Last edited: Oct 11, 2024
    C team likes this.
  19. C team

    C team Senior Member

    Joined:
    Nov 1, 2011
    Messages:
    249
    Location:
    Kent Island
    Greg, I'm a bit confused on how you mean to check the removed shore power cord and the 'pin' circuits. Can you give some detail?
    Sorry if I'm not getting the gist of the instructions.
  20. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,391
    Location:
    Satsuma, FL
    The ground pin or side tag on your shore cord should NOT have any continuity with any other pin.
    C team likes this.