Marine Air second air handler fan not kicking on

Discussion in 'HVAC' started by FLCranchi34, Apr 11, 2023.

  1. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    Marine Air second air handler fan not kicking on
    Owner of a 1997 Cranchi Zaffiro 34. Has a 16K Marine Air A/C and heat system with a Passport I/O controller. Boat has a galley/salon, a bow stateroom and a midships stateroom.

    System's compressor is located in the engine compartment and has two air handlers located under the galley seating, a 9k unit that conditions the galley and a 6k unit that conditions the two staterooms via a rheostat for the fan speed that's located in the forward stateroom.

    The issue: The fan for the 6k unit does not kick on when the compressor and rest of the system turns on, to include the fan for the 9k unit. Rheostat position does not cause the fan to come on. When power jumpered from the 9k fan power feed, the 6k fan comes on, but will cause the A/C circuit breaker to pop after about 7-10 seconds of operation.

    Second issue: 9k unit evaporator is icing up, initially at 65 deg commanded temp but also at 72 deg commanded temp. 6k unit evaporator is chilling, but only partially icing. I'm unsure if the two units are in series or parallel with regard to refrigerant flow. 9k unit icing could potentially be caused by lack of fan over the 6k unit?

    What's causing the 6k unit fan to not come on, and then trip the breaker when jumpered? I have the generic wiring diagrams for the system but I'm not seeing a clear issue. Obviously there's a short somewhere, but why not trip the breaker instantaneously?

    What's causing the 9k unit to freeze over? The 6k fan not removing the thermal cold load off the system?

    Thanks in advance!
  2. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,659
    Location:
    Satsuma, FL
    both evaps must have some air moving thru them or they will freeze.

    The Passport system can run on either 115 or 230Vac.
    The board only switches the L1 leg for either voltage.
    The L2 leg could be neutral or the second 115 of 230 volts.
    So, describe where and how your making this jumper again and what voltage your using?

    The passport has manual fan control also. Even without the compressor running, you can turn the fans on at various speeds.
    Does this work?
  3. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    Thanks Ralph, I suspected that was the case with the icing.
    Boat has a 30A 115V service.

    Jumper is 12 AWG wire using posi taps from the hot and neutral of the 9k fan power feed to the hot and neutral of the 6k fan power feed. Sounds like if the one leg was then powering both fans perhaps it pulled too much amperage and caused the breaker to pop. The system wiring diagram I have only shows one fan with L1 and L2 connected to it.
  4. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    The manual fan control at the I/O panel does control the fan speed on the 9k unit.
  5. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,659
    Location:
    Satsuma, FL
    I'm back with coffee, I started tilting hooch last night and didn't get back to this last night.
    Few more questions;
    Did this ever work correctly?
    6K fan came on when compressor was running or just with the panel on?
    Any recent work on the boat?
    Are you assuming that L1/L2 are standard black/white wires in making your test jump?
    Do you have a DVM to verify hot and neutral (to ground) during this test?
  6. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,659
    Location:
    Satsuma, FL
    I have to share a funny with you about that extra fan.

    I would wire the extra fan on the water pump L1 tag during installs.
    My partner wired it on the Compressor L1 tag.

    The old 3 knob controls were great, just tap from that control panel's raw fan voltage.

    Pending the day of the week, I'm sure its install varied where/how it was hooked up.

    My partner and I spent a day trying to figure out a dead cabin fan once.
    It was directly tied to the heads GFI outlet. Appeared factory.
  7. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    I also love a little hooch!

    Background: Bought the boat last November...I remember the 6k fan running during the survey as the exit ducting is loose on the front of it and so I felt the air coming out of it.

    No recent work on the boat, however it did set at the marina through the winter. The fresh water tank pump was replaced, as well as fuel filter service, oil change, drive oil change.

    Boat was towed 6 hours to get to its current location in February.

    As the wiring pigtails from the fans look identical, I tapped them on the pigtails on the matching colors. So yes, I'm assuming they're wired the same and L1 and L2 are the same colors at both fans.

    I do have a DVM, however I did not verify which was hot and which was neutral, see above regarding factory wiring, no work on this system since the survey, and the fact that the fan worked during the survey.
  8. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    Sounds like I need to try to trace the current power source for that fan and go from there. It almost looks like it comes from the 9k unit, over to the rheostat in the forward berth, and then back over to the 6k fan after going through a box of some kind.

    I'll try to post some pictures.
  9. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,659
    Location:
    Satsuma, FL
    Never trust color codes on a boat. Verify with a DVM.

    You may just have a blown fuse somewhere.
    Usually, C frame fans are used for the aux fans. If you can get compressed air or with power off get a finger near them, ensure they spin freely.
    C frames can overheat then pop fuses or breakers.
  10. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    Because of the ducting issue, I can shove my hand in there and it spins as easily as any other 12V squirrel cage fan I've ever encountered. I'm wondering if there's a relay or something out. Doesn't seem to need a starting capacitor for it.
  11. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,659
    Location:
    Satsuma, FL
    Any other 12v fan? For reference in ease of spin or a miss-type,,, not really the voltage?

    I've seen some weird stuff, I have to make sure.
  12. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,659
    Location:
    Satsuma, FL
    HA, You check the GFI outlets??
    Or extra breakers on the ACv panel?

    Follow the wires till you find the damage.
    Start at the condensing station any extra wires and go from there.

    Before you start pulling box covers off;
    You know what 120Vac feels like??
    You remember that it makes sparks?
    Are you comfortable working with electricity?

    Does your install look factory?
    No ships schematic?
    Last edited: Apr 12, 2023
  13. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    Automotive applications of roughly the same size, amperage, purpose, etc.
  14. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    Got it fixed. J box that had the circuit board inside it was a two unit version. Had spots for ships power, pump, unit 1, unit 2. Somehow the second unit was wired to the pump spot. I put it over onto the terminals for the first unit and it fired right up. System now works as advertised even though there was a large burnt spot on the circuit board...probably caused by when I back fed 12V into the "pump" terminals because it was wired that way. The unit two terminals had no power to them, and adding a jumper from unit 1 to them would have achieved the same thing.

    Bottom line, it now operates and does not ice up.
  15. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    Ok folks, new issue...same system.

    System ran all last year, put the boat back in this spring, ran for a bit, but now the system will not kick on. Controller lights up, there's a click from the compressor in the engine bay, silence for about 5 sec, another click, silence for another 5 sec and then it pops the breaker not for the A/C, but the double breaker for AC power on the panel.

    I disconnected the cooling pump and ohm'ed it, 17 ohms so I don't think the cooling pump is bad. Does this system require the cooling pump to start and be on line before the compressor starts? I pulled the control box apart and found it has a starting cap, a run cap, and a starting relay. I can only assuming the clicking is the relay.

    I'm solo at the moment and can't flip it on and make it into the engine compartment in time to hear which component the click is coming from.

    Any assistance would be appreciated.
  16. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,654
    Location:
    Miami, FL
    Yes the sea water pump needs to start before or at the same time as the compressor.

    The only way to know whether the pump is ok is to watch actual flow thru the unit If necessary temporarily rig the pump directly to power to check that.

    When is the last time the raw water side was descaled?

    if you have good flow, then the problem is likely to be with the compressor.

    If the main AC breaker is tripping instead of the unit, try to shut down other loads like water heater, charger etc and see how many amps it s pulling on a start.
  17. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    So I tested the distro block today on start up, no power to the pump, but there was power to the compressor. The starting relay clicks, but nothing happens. It has both a starting cap and a running cap, so has the starting cap failed?

    Only other AC power load is the battery charger, I'll drop that breaker and see if it doesn't blow the main then.

    Thanks for the reply Pascal.
  18. FLCranchi34

    FLCranchi34 New Member

    Joined:
    Mar 21, 2023
    Messages:
    23
    Location:
    Pensacola
    I replaced the start capacitor, system fired up, came out the next day and the system was on, blowing hot air, water pump running, but obviously not the compressor. I'll swap in a new run capacitor and see if that keeps it going, otherwise I'm guessing my compressor is toast?
  19. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,843
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    Do tou have a.clamp on amp meter that you can monitor thhe compressor current while trying run it ?
  20. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,659
    Location:
    Satsuma, FL
    Or watch your ships amp meters swing when the compressor tries to start?