Click for YF Listing Service Click for Abeking Click for CL Yachts 99X Click for Westport Click for Ocean Alexander

AquaAir Chiller Keeps faulting

Discussion in 'HVAC' started by Danvilletim, Jun 24, 2021.

You need to be registered and signed in to view this content.
  1. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca
    On the new to me boat we just got, there is a two 5-Ton Chillers feeding the chiller loop system - AquaAir is the system / brain. One chiller is brand new (Ocean Breeze). We use a sea chest to feed these

    We have been have many faults.. Low Pressure Refrig / High Pressure Refrig / Flow Switch. We tried our best and paid a couple 1000 to have West Palm Beach techs tackle this.. They said we were good :) Descaled, tested, etc.

    Its been fault out non stop while underway... Same 3 faults listed above.. At night at the Marina is seems to be okay? Sea Chest was cleaned on Tues.... What could make it get not get good water flow while underway?
  2. gcsi

    gcsi Senior Member

    Joined:
    Mar 18, 2011
    Messages:
    131
    Location:
    tampa
    First thought would be to crack open the sea chest while under way and note water flow, then repeat at rest looking for a large delta between both flow rates. If water flow is equal, should rule out any issues “outside” the system.
  3. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,950
    Location:
    Miami, FL
    The faults you mentioned have very different causes. Low pressure is obviously just that but if you ve had the system serviced then they should have checked the pressures. Are both chillers showing low pressure ??

    High pressure on the other hand is almost always a lack of water flow or dirty condensers. Can you observe the overboard discharge?

    flow switch issues are just as unrelated since that’s an issue with the chilled water loop. Could be air in the loop or a circulation pump problem.

    just find it odd that you re having all three unrelated faults at the same time.
    captainwjm likes this.
  4. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    14,585
    Location:
    Satsuma, FL
    One of the negatives of sea chest, when poorly designed, no top vents and water customers mounted on the top of the tower (ACs?), lots of foam gets pumped to the equipment.
    For the old salts, I learned of these issues on a 44 alloy Striker many (MANY) moons ago.

    Yep, all settled down while dockside.
    T.T. likes this.
  5. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca
    Yup just docked after 16 hours on the ICW after it turned into 6-8 outside Brunswick. And it’s starting to cool.

    I’m curious about the comments on venting the sea chest? What’s that mean. One weird think is port water level is 8 inches lower than starboard in the see thru sea chest. Haven’t cracked that on this trip and assumed it’s holding air. Getting a sep strainer next hull out but for the summer I got to get cool! Wife’s surprise birthday party cruise in the new boat on Sat. Got time to try a few things.

    The raw water pump looks like crap and had a pile of salt around it. Regardless Im replacing it. Maybe a weak pump struggles to pull water when under way and the c30 is sipping from same straw? Just guessing. Sea chest is pretty big. Twice the size of the ole Striker!
  6. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca

    I used to be able to see the water flow but after adding 4000 gal it’s under water.
  7. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,904
    Location:
    Fort Lauderdale
    That boat will never be cool over the summer, 10 tons isn't even remotely close to what a yacht that size needs.

    You have 2 different brands of chillers?

    That being said, if the water level is 8" below on that sea chest versus the other one, while the engine is running, the thru-hull isn't nearly big enough (or it's got a grate or barnacles inside the opening restricting waterflow) to feed both the engine and A/C and the engine sucks harder so it wins the battle.

    Some yachts have a vent hose from the lid up really high in the air, it allows any air that gets sucked into the seachest to escape, without having to be sucked through the equipment to get out.......
  8. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,950
    Location:
    Miami, FL
    Can you easily get to the discharge ? If so put in a tee and a couple of valves. Route one leg of the tee to a 5 gal pail. Flip the valves to divert discharge to pail. Time how long it takes to fill the pail at the dock and under way.

    if the pump has salt outside it means it’s leaking. What kind of pump ? Oberdorfers and the likes have metal impellers which erode with time. How old is it? Start by replacing the pump and getting the old one rebuilt as a spare if even possible.
  9. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,950
    Location:
    Miami, FL
    I agree with J. 10 tons isn’t enough to keep the boat cool during the day in summer time... at night you ll
    be ok but not during the day. What is the loop temperature during the day and at night ?

    Two different brands of chillers is a red flag as well... yea in theory the Ocean Breeze should get along with the AquaAie controls but who know... maybe that’s why you re having these contradictory errors

    another concern is the raw water discharge being underwater with full tanks.
  10. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca
    Great feedback. Documentation on this boat sucks.

    I have a receipt for the ocean breeze which is 5 ton. I have to assume the other is 5. Boat can be 74 in day in SoFl when it doesn’t fault at the dock. Would like colder but not bad for June. Perhaps when it’s time we can up size capacity.

    I want to order a new pump today. Can’t seem to find a price pump cd100 pump. It’s 70gpm. I found another brand that’s 85gpm. Id assume the brand pump is irrelevant as long as fittings and capacity are good.
  11. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    14,585
    Location:
    Satsuma, FL
    Skippy J got it.
    In rough water or running bow high, our ole sea chests would fill with foam and air. The new saloon A/C would kick out with a high pressure trip.
    Took a while to figure it out. Ran an experimental hose from a chest top cock to the ER air inlet drain box. That worked good and then the boat sold.

    Never knew we were having sea chest issues until the ole 3 knob system was replaced. No error codes from a 3 knob panel.
  12. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca
    Mystery not solved. We have no air or frothing in that sea chest. It was full to brim and still faulting. I think pump is weak and can’t over come main like J says but it’s still a guess.
  13. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    14,585
    Location:
    Satsuma, FL
    While your running was what I was thinking.
    Dockside by now the chest would be full. Outside, in the chop may have been different.
  14. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,950
    Location:
    Miami, FL
    Check out Scott pumps. That’s what we had on the 84 and now the 116. Very good pumps both for the loop and sea water. I replaced the sea water pump 3 years ago as the impeller was eroded and had it rebuilt as a spare. Pretty sure it was original to the boat or 8 years old then

    I prefer March but I don’t think they make them that big.
  15. bayoubud

    bayoubud Senior Member

    Joined:
    Feb 19, 2017
    Messages:
    1,148
    Location:
    Florida
    You might try contacting Tropical Marine Air Conditioning in Lauderdale, they were a large dealer for Aqua Air when they shut down. We bought some spare parts from them. If you are getting low flow on the loop it is probably air. You can program their air handlers to run continuous for four hours which is good for clearing any air in the loop if you have automatic air vents and bleed highest air handler. Easy to troubleshoot the low flow switch and replace if needed. Be careful with tech descaling the loop, it can cause leaks on the a/h copper plumbing connections. Also a reset to factory default can sometimes cure false readings. The new pump may fix the high pressure default. The CD100 pump is cast iron, the Scott pump Pascal recommended is a much better bronze pump.
  16. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,904
    Location:
    Fort Lauderdale
    I'm confused, in post #5 you stated that port water level is 8" lower than starboard seachest water level.

    The other thing with vented seachest, is you know if the thru hull is restricted because the vent will allow it to suck the seachest water level down.

    A/c pick ups should NEVER be on a sea chest.
  17. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca
    Chiller is pulling from Starboard CHS which has the water level at the very top. Port see chest is about 8 inches lower. This fantasy chess concept seems interesting. I still need to replace the pump because it looks like it’s leaking.
  18. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,904
    Location:
    Fort Lauderdale
    absolutely replace the pump. See if you can plumb in a water pressure gauge after the pump. Watermaker companies use them and sell them. It will tell you exactly what's going on. See what the pressure is at the dock and see what the pressure is at cruise, will also tell you if the seacock is getting clogged.
  19. bayoubud

    bayoubud Senior Member

    Joined:
    Feb 19, 2017
    Messages:
    1,148
    Location:
    Florida
    I had a cd100 water pump that was rusting badly on my last boat with twin 4 ton Aqua Air chillers. Replaced with the Scott bronze pump with zero problems. Thinking the cd100 pump was Aqua Air's own part number. Check with Tropical Marine Air.
    Thought I would pass on when the boat recently sold the new owner had a Electro Clean electro-chlorinator installed between the ac thru- hull and strainer. On start up the flow was 15 gpm, after 3 weeks the flow was 16 to 17 gpm, and now at 2 months reported at 17 to 18 gpm with no maintenance other than cleaning sea grass from the basket. Doubt it would work on the sea chest and not recommended for engine raw water use. Also claim it does not harm the cooper-nickel alloys. So, they do work and save continuous cleaning with corrosive chemicals. We lost both of our chillers because of previous aggressive cleaning with corrosive acid cleaners at considerable replacement cost. Makes the unit installed easily pay for initial cost in several years with reduced maintenance and a longer life. If you add a thru-hull for the chillers you might want to consider the Electro Clean, they apparently work well. J's suggestion to add a pressure gauge is a good idea for monitoring flow and maintenance needs.
  20. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,904
    Location:
    Fort Lauderdale
    I'm dealing with a yacht right now with a 1 year old electro clean system, while the a/c strainer doesn't seem to get much algae build up on it, it certainly is getting a lot of barnacles growing on it. So not thoroughly impressed over my own methods of using bromine tablets.