Click for Cross Click for Walker Click for Perko Click for Furuno Click for Northern Lights

Shorepower issues

Discussion in 'Neptunus Yacht' started by Worthyvess, Aug 13, 2019.

You need to be registered and signed in to view this content.
  1. Worthy vessel

    Worthy vessel Member

    Joined:
    Feb 16, 2019
    Messages:
    83
    Location:
    Sarasota
    The boat does have isolation transformers but I do not know how that affects my issues of extending the power cord or running off one 50 amp cord
  2. Worthy vessel

    Worthy vessel Member

    Joined:
    Feb 16, 2019
    Messages:
    83
    Location:
    Sarasota
    If I used a y adaptor connecting the boats two 50 amp cords to a single 50 would that work?
  3. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,756
    Location:
    Vero Beach

    The difference between a 3 and 4 wire cord is simply that you aren't carrying the ground with the 3 wire version, only 2 lines and 1 neutral. Your ground is isolated aboard from shore. You could just as easily use a mare standard 4 wire cord, as the ground is transferred through the round metal portion of the plug housing. You still have only 3 prongs, 2 for line and 1 for neutral.

    It's a bit hard to understand what you're facing as we don't know how your shore power feeds your panel system in comparison to how it is fed by generator.

    Check your battery chargers. The input voltage should be listed on the identification plate. Why one is 12o and the other 240 was likely someone thinking they were trying to balance their load. Good idea to simply do the math of amp requirements for each circuit on each line of the panel. Listing that information out on a piece of paper will help you to better understand the existing load balance, requirements, and path to managing the loads so that you can run the priority items.
  4. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,756
    Location:
    Vero Beach
    The isolation transformers are simply stripping the ground from shore and allowing the vessel to use its own bonding system, separating it from the shore circuitry.
  5. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,756
    Location:
    Vero Beach
    No. You can only run 50 amps through a shore cord rated for 50 amps. To use a smart Y you'd need heavier cable from the pedestal all the way to your panel's main breakers. And then you'd need apparently to reconfigure the incoming power on your panel. Your panel appears (from the shore side) to be separated into groups allowing you to manage and spread the load. Best guess is that it was set up properly and you're simply going through your learning curve of how to make it work.

    What did your surveyor tell you about this setup? Did he review and comment? If he didn't, and if you're in Ft Lauderdale, you might consider having Wards come out and do an electrical survey and provide you both with their review as well as their interpretation and advise. You'd learn a lot during that process of both how things work in your setting as well as what their recommendations are. Bad power setups are a big problem both for you as well as for the boats around you.
  6. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,756
    Location:
    Vero Beach
    Sarasota, consider calling JTB out of St Pete if you don't already have a resource.
  7. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,756
    Location:
    Vero Beach
    Also, reading back to your initial post, your boat should likely be set to allow you to run one AC on the one cord. I can run most of my systems and one 5 ton chiller on a 50 amp service (can't cook, too). If I need the other chiller, too, I need to run off my 100 amp setup. If your main cord plugged, does it provide power to only one chiller or to all three? I'm trying to get a sense of how your AC side is set up to distribute incoming power from shore...
  8. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,498
    Location:
    Satsuma, FL
    Isolation Transformers take 230Vac and make 230/120. It makes it's own neutral.
    Fault current from the transformer to shore is still (always) required.
    This makes the 3 wire shore cord (No Neutral wire).
    Onboard, Fault current may be released to the bonding system and the water or tied to shore.
    I like the idea of galvanic isolation and a tie to shore if divers go under your boat often.
    PM me for some schematics if needed.
    Last edited: Oct 26, 2019
  9. DOCKMASTER

    DOCKMASTER Senior Member

    Joined:
    Feb 26, 2012
    Messages:
    1,503
    Location:
    Ketchikan, Alaska
    I don’t know if this is applicable to your issue but on my 50amp shore connection I had lots of trouble with the wiring to the shore power receptacle on the boat and the twist lock plug. In fact, one time I lost shore power and pulled the receptacle and could clearly see burn spots. I replaced the boat’s receptacle and the boat end plug on the cord with a 50 amp Smart Plug. Huge difference. No issues since, cord doesn’t get hot and I’m able to run more by having a much more solid connection in that plug and receptacle. It’s also easier to plug and unplug. I would gladly pay to change the marina side as well but they won’t let me. And no, I’m not a paid spokesperson or dealer for Smart Plug. Just very happy with the product.
  10. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,570
    Location:
    Miami, FL
    Hmmmm. I meant two hots/ one ground / no neutral
  11. bayoubud

    bayoubud Senior Member

    Joined:
    Feb 19, 2017
    Messages:
    1,149
    Location:
    Florida
    Seems you should be able to run the AC on the house cord with high amp equipment off. You would need a transfer switch to combine House and AC at the main panel otherwise you would always need two cords if wired separately. Check shore cable connections and voltage. Check voltage at chiller breakers. Could just be a bad connection somewhere on shore power. How many amps are you drawing when on the generator, with and without the chillers vs shore power?
  12. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,570
    Location:
    Miami, FL

    Wrong. I know my earlier typo made things even more confusing but with isolation transformer the shorepower cord carries TWO HOTS and GROUND. it does not being neutral on board as neutral is created but the tranaformer(s)
  13. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,540
    Location:
    Fort Lauderdale
    Yes, they are standard on Neptunus such as the OP's. You can only run 1 chiller and the rest of the boat on 1-50 amp cord on a 62' Neptunus without tripping breakers usually unless the water heater and some other stuff is off. 2 Chillers will usually trip the breaker if you have the hot water heater, refrigerator and ice maker or two all on and a couple things happen to start at the same time....…….
  14. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,540
    Location:
    Fort Lauderdale
    Is your extension cord a marinco with plastic ends, or a hubbel with metal ends? You might need metal ends for it to properly complete the circuit to the extension cord/land. If you are 100% sure that your 50 amp (extension) cord is good and the dock power is correct. You have something mis-wired on the boat is what it sounds like to me.

    Every Neptunus I've run 55' and 62', you were able to run off of one cord. Please take a picture of your electrical panel where the breakers are to select shorecord 1, shorecord 2, generator etc.
  15. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,756
    Location:
    Vero Beach
    Isolation transformers work in precisely the same manner as polarizations transformers, they ensure proper polarity regardless of dock wiring, with one important distinction; the dockside green safety grounding wire is isolated from the vessel’s green safety grounding, bonding, or DC negative wiring. Why the separation and what’s the value and risk to such an arrangement? The isolation of the grounding systems achieves one additional goal for an isolation transformer—it reduces the possibility of “foreign” or other boat-induced stray current or galvanic corrosion.
    aboas likes this.
  16. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,540
    Location:
    Fort Lauderdale
    One other question. Has the end on your boats shorepower cord been replaced? Or is it the factory molded Glenndenning plug still on it?
  17. Worthy vessel

    Worthy vessel Member

    Joined:
    Feb 16, 2019
    Messages:
    83
    Location:
    Sarasota
    Don’t know
    But it is 50 amp 125/250v
  18. Worthy vessel

    Worthy vessel Member

    Joined:
    Feb 16, 2019
    Messages:
    83
    Location:
    Sarasota
    This is with the gen running
    Shore power off BAFB6DEB-5BE3-4533-A4A4-5E5ACC7A1956.jpeg
  19. Worthy vessel

    Worthy vessel Member

    Joined:
    Feb 16, 2019
    Messages:
    83
    Location:
    Sarasota
    98B45B9F-84A6-49B8-A854-C2E7DB74A28A.jpeg
  20. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,498
    Location:
    Satsuma, FL
    More correct word would be "may".
    The green wire to the shore service can be configured different ways.
    Total isolation from the shore service makes any fault current to release thru your ship to the water.
    We encourage the idea of galvanic isolation and a tie to shore if divers go under your boat often.