Click for Burger Click for YF Listing Service Click for Northern Lights Click for CL Yachts 99X Click for Delta

Chiller recommendations

Discussion in 'HVAC' started by Danvilletim, May 11, 2019.

You need to be registered and signed in to view this content.
  1. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,884
    Location:
    Fort Lauderdale
    It sounds to me like you need to get a new air conditioning company. Need to find out what the code is. But if both soft starts are doing it, with 2 new chillers, there's an issue.

    It also could be a shorepower issue and the chillers are not getting enough voltage. Also, if the soft starts are winding up too slowly, it could cause issues.
  2. captholli

    captholli Senior Member

    Joined:
    Jan 4, 2010
    Messages:
    1,214
    Location:
    In The Bilge
    First thing is to identify the "F-2" code on your VFD's , Should be simple as your only getting one error code and not multiples. VFD's are used for supplying clean pure sine voltage when powering up or "spooling" up your compressors to take away the instant current in-rush of a hard compressor start. Obviously they should be of the proper H.P. to handle one chiller each and the VFD has to have an initial programing of parameters matching your system. I would recommend a re-program of the parameters of both VFD's to be the first line of trouble shooting. The chiller itself has protection circuits for compressor pre-heat, low water flow , high head, etc. and will code on its own panels and not the VFD's so if you have a problem with your chiller drawing high current to overload a drive than it would knock your drive off line and you would code on your chiller panel also. Most installs will have secondary bypass switch's installed for the VFD's when they fail because sooner or later one will go on you when you least expect it to and then you can run your system the old fashioned way without the VFD's and watch your lights dim when compressors hard start Funny thing is that most if not all units (compressors) in newer marine applications are scroll compressors that really don't need VFD's for current in-rush but they're prevalent because of the clean voltage /sine issues.
  3. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca
    Ok. The code is FLF and is low voltage under 200v. And I think I might have discovered the issue. Thought I’m not sure. The freq drive is not set to auto restart. So once voltage goes below 200v is faults. This would also be the case when switching from shore power. Do you see anything wrong w putting it into auto restart. The Ac tech doesn’t want to do it but doesn’t get that in so Florida I can t have Ac down for 3-4 days bet visits.
  4. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,930
    Location:
    Miami, FL
    The big question is why does the voltage drop under 200v. Not good. When switching from shore to gen, the system will shut down anyway and should restart. Rotary switches if that’s what you have should not be switched underload. Turn off the air cons and other heavy loads, transfer power and restart
  5. bayoubud

    bayoubud Senior Member

    Joined:
    Feb 19, 2017
    Messages:
    1,148
    Location:
    Florida
    You could run dehumidifiers (maybe rent) while not on board the boat until resolving the shore power problem. We run one along with the ac in the master plumbed with a hose to the shower drain with when at the dock, leave the air handlers running on low for circulation. Keeps the humidity down on the lower deck.
    Last edited: Jul 31, 2019
  6. wdrzal

    wdrzal Senior Member

    Joined:
    Feb 6, 2006
    Messages:
    415
    Location:
    Allegheny Mountains of Western Pa
    Once a compressor shuts down it takes up to several minutes until the high side equalizes with the low side so they can restart. This delay is programed into either the AC controller or sometimes the frequency drives. Usually the compressors thermal protection trips if a premature restart is tried, they are self resetting once they cool (several minutes)l. Sometimes a breaker kicks or frequency drive locks out, depending on how the system was designed. This might be why the AC tech didn't want the drives to auto reset. If you can program the frequency drives to auto restart set the delay to at least 3 minutes. You should never see 200 volts, I would hunt down that problem. Pascals advice in post 44 should be followed when switching from shore to internal power or back. Generators can have sine wave problems but the grid, at least in the USA is a very stable 60 HZ.
  7. chesapeake46

    chesapeake46 Senior Member

    Joined:
    Jul 26, 2009
    Messages:
    1,873
    Location:
    Chesapeake Bay, Delaware Bay & S.Jersey
    It would be helpful to monitor the shore power voltage too. A 208 volt service, which is a common 3 phase commercial service could easily drop to 200 volts during times of high demand.

    The freq drives may be doing their job properly by protecting themselves from low voltage.

    Brings us back to the manual. That would tell you the voltage thresholds and whether you can safely lower that parameter.
  8. wdrzal

    wdrzal Senior Member

    Joined:
    Feb 6, 2006
    Messages:
    415
    Location:
    Allegheny Mountains of Western Pa
    First a question ? is your boat wired for 3 phase power. 208 volts is usually the high leg ( L3 ) of a 3 phase transformer installation. 208 volts to neutral/ground. L1 and L2 should be 120 volts to neutral/ground and 240 volts between L1 to L2. Unless your wired for 3 phase power you should not be connected to that leg (L3).
  9. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca
    We are 100 amp single phase. We have never been able to measure less than 230v but I’m sure it happens. That’s a good suggestion on the delay. I’ll see if our AcTech freq drives can support a delay.

    Any yes normally we shutdown chillers when switching from shore power.
  10. Danvilletim

    Danvilletim Senior Member

    Joined:
    Oct 30, 2011
    Messages:
    794
    Location:
    isleton, ca
    Would the Booster Trasformer prevent from voltage drops?
  11. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,884
    Location:
    Fort Lauderdale
    It should help. What I think might be happening is that both chillers are coming online at the very same time causing the voltage drop. Check and see if you can change the delay on 1 of the chillers. It's also possible that your 100 amp service is simply not enough and with chiller 1 already running and number 2 coming online the voltage stops dropping. The other side of the coin is when you're away you can run only 1 chiller and it should help. A yacht of your size should have full time crew on it (everyday).
  12. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,930
    Location:
    Miami, FL
    100amp is tight for us (84 Lazzara) in July and August. We can run both chillers and regular loads but add in an oven or a dryer and breaker goes pop.

    No error on the Drives though, just the breaker by the glendining. No big deal from late afternoon till late morning when one chiller is enough.
  13. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,979
    Location:
    Vero Beach
    My chillers have temp controls that monitor the chiller loop as it passes each chiller. The temp settings are staggered so that only one unit is called to handle the cooling, but if the high side hits another threshold, the second unit is called to assist. I believe #1 is set at 44/54 and #2 is set at 46/56. The second unit only runs on the warmest of days. The temp settings can be adjusted quite easily for both engage and disengage temps.
  14. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,979
    Location:
    Vero Beach
    I can run both chillers, cook, and wash clothes. Have you looked at the status of the water heaters? Are they creeping up with amperage demand? My Acme system and most transformer both provide a full compliment of voltage, so that helps with the load, too. But I really don't have any trouble aboard if I have the full 100 amp supply.
  15. wdrzal

    wdrzal Senior Member

    Joined:
    Feb 6, 2006
    Messages:
    415
    Location:
    Allegheny Mountains of Western Pa
    NO.....If the primary side of a transformer drops in voltage so will the secondary side. IF you install a boost transformer to boost volts you drop down in amperage.
  16. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    14,523
    Location:
    Satsuma, FL
    Problem goes away on Gen-Set?
    Your ISO transformers in boost mode?

    How long does it take the freq drives to bring the pumps to speed?
    Can you determine is it when the pumps are coming up to speed or already running?

    I understand strange questions, just something for me to chew on in my sleep.
  17. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    14,523
    Location:
    Satsuma, FL
    Nothing is for free. you want volts, you have to give up amps. Hence a question in post # 56.

    W=VxA
    Raise the V, A must go down. The motor will draw it's watts. If not enough of any of these three, things smoke and breakers trip
  18. wdrzal

    wdrzal Senior Member

    Joined:
    Feb 6, 2006
    Messages:
    415
    Location:
    Allegheny Mountains of Western Pa
    Even if the frequency drives give you a "slow start" the compressors still will draw any where from 150% to 300% of there ratings for a couple seconds. If that's the case, the AC units may just need capacitors added to smooth this currant draw out for that short period. Search for "hard start AC capacitors".
  19. rtrafford

    rtrafford Senior Member

    Joined:
    Jul 13, 2019
    Messages:
    1,979
    Location:
    Vero Beach
    If the problem in voltage is dockside, take a walk and check the plate on the marina transformer. Likely it's converting to 208, coupled with long runs of wires, and you'll be at 200 at your pedestal. Then you'll have another drop via your shore cord. I've run this exercise after discovering 196 volts aboard. I only had 200 at the pedestal under load. The transformer was providing 208, and the delivery was several hundred feet. I was able to install a 25 KVa boost transformer at the panel, boosting 208 to 240. Now I'm at 230v entering the boat, and my boost aboard kicks that up easily. Problems were solved.
  20. wdrzal

    wdrzal Senior Member

    Joined:
    Feb 6, 2006
    Messages:
    415
    Location:
    Allegheny Mountains of Western Pa
    To me, a good HVAC electrician should be able to figure this out in under a hour since its repeatable. The installer or marina might not want to fess up to a obvious problem or doesn't know how to trouble shoot it or correct it. You may need a independent electrician familiar with commercial power ,AC and frequency drives. Just because a person sales and installs a system doesn't mean they understand how it works on a fundamental level.