Click for Westport Click for CL Yachts Click for YF Listing Service Click for Burger Click for Nordhavn

Marineair chillers replacement or repair

Discussion in 'HVAC' started by Pacmac, Aug 10, 2016.

You need to be registered and signed in to view this content.
  1. Pacmac

    Pacmac New Member

    Joined:
    Aug 8, 2016
    Messages:
    13
    Location:
    Vancouver b.c. Canada
    This might be a long post,so I will apologize for that. We have three chillers in our engine room providing chilled water to our fan coils thru out the boat. The chillers in turn are cooled by raw water. Two of the chillers are now not working. One will not hold refrigerant the other has leaked a brown oil substance, that might be compressor oil. The system is five tons per chiller. The boat was in Florida and the Bahamas from 2010 until last year when I brought it to Vancouver Canada. One chiller in Vancouver is sufficient for our Summer's but I would feel better having at least two just in case one goes down.

    I have had a marine air guy look at this issue and he suggest replacing two of the chillers and removing the working one as he feels it's only a matter of time before it becomes non operative. The cost of each replacement chiller is approx 13,000.00 plus labor. Dose this seem reasonable, is 6 years the life of a chiller, and can't these chillers be repaired. I don't have a lot of experience in this so I welcome your knowledge. Fred
  2. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,938
    Location:
    Miami, FL
    They should last longer than 6 years and $13k for each chiller alone seems high but what size are they?
  3. Pacmac

    Pacmac New Member

    Joined:
    Aug 8, 2016
    Messages:
    13
    Location:
    Vancouver b.c. Canada
    5 tons, 180000 btu's
  4. wdrzal

    wdrzal Senior Member

    Joined:
    Feb 6, 2006
    Messages:
    415
    Location:
    Allegheny Mountains of Western Pa
    5 tons = 60,000 BTU
  5. olderboater

    olderboater Senior Member

    Joined:
    Sep 2, 2013
    Messages:
    7,127
    Location:
    Fort Lauderdale
    5 tons each x 3 = 180000 btu's total.
  6. Pacmac

    Pacmac New Member

    Joined:
    Aug 8, 2016
    Messages:
    13
    Location:
    Vancouver b.c. Canada
    Yes thanks that's right. What's your opinion on the issues. Fred
  7. FIQ

    FIQ Member

    Joined:
    Feb 19, 2016
    Messages:
    60
    Location:
    Olympia, Wa
    Sounds like you have 2 units with refrigeration leaks.
    If you see oil, then you have a leak.
    Did the tech find the locations of the leaks?
    You can use soapy water and spray the lines, joints and the tube bundle shell.
    You may also have a leak in the tube bundle.
    Even if you have to replace the tube bundle, it shouldn't have to be overly expensive!
    Repair the leak, replace the filter/drier, and charge the system..
    Don't forget to descale the raw water side once in a while, to prevent frozen tubes.
  8. Pacmac

    Pacmac New Member

    Joined:
    Aug 8, 2016
    Messages:
    13
    Location:
    Vancouver b.c. Canada
    Thanks. We will look into this. The thought is that the leaks are in the heat exchanger.
  9. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,887
    Location:
    Fort Lauderdale
    Are you saying that all of the chillers are 2010??? I would find a new A/C guy immediately. Sounds like he just wants to sell units. Chillers that are properly installed should last 10-12 years usually. 6 years is very premature. I would absolutely NOT remove the working chiller. The question is why are these chillers failing so early. I would check freon pressure in the one that is running and see if it is overcharged. The chillers are fixable, but need to determine where the leaks are. It might be possible to make one good one out of the 2 that are not functioning or repair both of the non functioning ones. Retail price on a MCGx60 is $11,770.00 per Dometics 2016 price book. If you want smart start, which I'd highly recommend retail price is $12,235.00.
  10. DOCKMASTER

    DOCKMASTER Senior Member

    Joined:
    Feb 26, 2012
    Messages:
    1,661
    Location:
    Ketchikan, Alaska
    I replaced both my chillers season before last. I don't think they were quite as many BTU's as yours but I can't recall the actual size. They are Dometic Compact units. One was still working but the reversing valve on the other was stuck. Mine are difficult to get to and have to be pulled to service them. Since they were original to the boat (1994 model) I decided to replace both. The units were about $4,500 each for the parts.
    I'm in a similar climate to you but keep in mind these units also provide your heat unless you use a separate heating system. I used Cliff's Marine Service out of Seattle as they are a local Dometic dealer and Cliff is pretty knowledgeable. Installation was pretty straight forward as it is just reconnecting some pipes and electrical.
    If you only got 6 years of service on yours I would say something else is wrong in the system to cause failure that early. You have to be careful that your piping loop doesn't freeze in the winter unless you have the proper solution. I drained mine as it only had water. Filled it back with the recommended glycol solution and bled all the air handlers. It was a bit of a pain to get it all bled but worked much better than ever before once it was all done. It was also recommended to regularly cycle my units and switch them from a/c to heat a few times so things don't seize up.
  11. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,887
    Location:
    Fort Lauderdale
    Generally you can bleed all of the air out from the highest unit in the system, like if you have a flybridge mounted air handler.
  12. Scott M

    Scott M Member

    Joined:
    Mar 9, 2016
    Messages:
    72
    Location:
    Annapolis, MD
    I have a similar system set up (although smaller total BTU) and had an experience that I wanted to highlight. Got repeated Low Pressure alarms. Would refill Freon and would alarm again within a few days. Discovered one of my chillers had multiple pin hole leaks that made repair impossible. The culprit turned out to be that the unit was NOT bonded to the whole boat bonding system. The adjacent unit, which was adequately bonded, has continued to operate without an issue. Had to replace the one unit ($5-6k +labor). These units definitely should last longer than 6 years. Most industry people will say 10-12 years. Similar to a home heat pump. Although...5 years in FL is like 10+ years everywhere else. Hope this helps!
  13. Pacmac

    Pacmac New Member

    Joined:
    Aug 8, 2016
    Messages:
    13
    Location:
    Vancouver b.c. Canada
    We are going to pull the three units and have them inspected to see what's going on. Since my first post the fresh water fill gauge is loosing pressure which means I must have a leak in the system. I will report my findings in the latter part of September.
  14. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,887
    Location:
    Fort Lauderdale
    Inspected??? By whom? The tech should be able to inspect them on board as long as access is decent. Gauges should tell you how they're running.......Again, you need a different tech.
  15. Pascal

    Pascal Senior Member

    Joined:
    Feb 29, 2008
    Messages:
    8,938
    Location:
    Miami, FL
    If you re loosing pressure in the fresh water loop it could be a number of things including a leak at a air handler incl a bleeding valve, or just at a fitting somewhere. This is not a reason to pull the chillers.

    I agree, find a tech who knows what he s doing
  16. DOCKMASTER

    DOCKMASTER Senior Member

    Joined:
    Feb 26, 2012
    Messages:
    1,661
    Location:
    Ketchikan, Alaska
    Agree with Capt J and Pascal. Are you having to add fluid to the piping loop? Pressure loss can be coming from lots of places in the system. Honestly, a fluid leak at the chillers should be easy to spot but is one of the less likely places for a leak. As suggested, any of the air handlers, bleeders or fittings could be an issue. You also could have a circulating pump that is getting worn and just not building pressure. Many of these systems have the ability to add water to the loop direct from your fresh water system and there would be an isolation valve and a check valve or back-flow preventer so the glycol mixture can't get back into your fresh water. You might want to check there to ensure you are not leaking pressure at either of those valves. Last but not least, have you verified the gauge you are relying on is accurate and reading properly?
  17. Pacmac

    Pacmac New Member

    Joined:
    Aug 8, 2016
    Messages:
    13
    Location:
    Vancouver b.c. Canada
    Thanks for the feed back. The two chillers that we want to get on a bench are non operational. One will not hold a charge and the other leaked a bunch of brown oily fluid from it. The number one chiller is still working but the loop water pressure is low. We have a in line filler and when we open the valve the pressure goes up, but as soon as we turn it off the pressure goes down.
  18. Capt J

    Capt J Senior Member

    Joined:
    Jul 11, 2005
    Messages:
    14,887
    Location:
    Fort Lauderdale
    Does it hold pressure once it goes down? You might have to add for a while in 30 second bursts as the water/ coolant works it's way through the system, especially as the pump is running. Quite honestly, you need a more knowledgable tech.
  19. Pacmac

    Pacmac New Member

    Joined:
    Aug 8, 2016
    Messages:
    13
    Location:
    Vancouver b.c. Canada
    It dose not hold pressure once the unit stops. We are 10 days from seeing a tech. There are three techs in our area. I will give one of them a call when we get home to get his evaluation before we do anything else. We have not been able to find the leak as of yet. Thanks for your help.
  20. Pacmac

    Pacmac New Member

    Joined:
    Aug 8, 2016
    Messages:
    13
    Location:
    Vancouver b.c. Canada
    Well we finally found the leak. It was behind the wall in the master stateroom closest. The plastic elbow had a split in it. We will repair it when we get home and then get another tech to come in and reset the system up. Thanks for your help.