355 kohler issue

Discussion in 'Carver Yacht' started by seldomdry, May 20, 2013.

You need to be registered and signed in to view this content.
  1. seldomdry

    seldomdry Member

    Joined:
    Oct 10, 2012
    Messages:
    79
    Location:
    Stillwater MN
    OK. I have no gen power to #2 relay. Power from gen to #1 and power to both with shore power pluged in. Genny fine has to be a wiring issue. It all worked last season...
    Any ideas??
  2. NYCAP123

    NYCAP123 Senior Member

    Joined:
    Mar 14, 2008
    Messages:
    11,208
    Location:
    Long Island, NY
    Sounds like a problem at or with the main source breaker.
  3. seldomdry

    seldomdry Member

    Joined:
    Oct 10, 2012
    Messages:
    79
    Location:
    Stillwater MN
    No that is not a problem. I have a auto relay for shore power and Genny. I have shore power juice to relay but no gen power to relay..
  4. K1W1

    K1W1 Senior Member

    Joined:
    Sep 30, 2005
    Messages:
    7,427
    Location:
    My Office
    Hi,

    Is your genset actually producing electricity?
  5. seldomdry

    seldomdry Member

    Joined:
    Oct 10, 2012
    Messages:
    79
    Location:
    Stillwater MN
    Yes. Have power to #1 relay. #2 no power to Shore Power/Gen relay....
  6. n36511

    n36511 New Member

    Joined:
    Feb 7, 2013
    Messages:
    34
    Location:
    Lake Lanier, GA
    If not getting juice to the relay, I would check the generator control panel. There is usually a circuit breaker for each leg of out put. The breaker could be shot.
  7. sam356

    sam356 Member

    Joined:
    Oct 31, 2011
    Messages:
    125
    Location:
    Great Oaks Fairlee Creek MD
    Did you running the gen with the shore power on.
  8. seldomdry

    seldomdry Member

    Joined:
    Oct 10, 2012
    Messages:
    79
    Location:
    Stillwater MN
    I dont think both both were hooked at the same time. What if it was?? If it was wouldnt the relay control that issue?
  9. NYCAP123

    NYCAP123 Senior Member

    Joined:
    Mar 14, 2008
    Messages:
    11,208
    Location:
    Long Island, NY
    You can run the gen while on shore power, and it will have no effect. You're blocked from feeding the panel from both sources.
  10. Capt Ralph

    Capt Ralph Senior Member

    Joined:
    Sep 8, 2004
    Messages:
    13,389
    Location:
    Satsuma, FL
    I remember working on a boat that used breakers and a sliding bar to keep shore power & gen-set apart. Well one of the breakers was found bad, internal short or carbon trace. Shore power took out the diodes in the gen-set.
    The owner did then mention, he got a buzz handling the shore power cord while the gen-set was running.

    Do not trust those breakers as off or isolator switches. Nothing beats a good trusty rotary switch.
    ,rc
  11. sam356

    sam356 Member

    Joined:
    Oct 31, 2011
    Messages:
    125
    Location:
    Great Oaks Fairlee Creek MD
    I know that cavers did not come with switch for shore power or gen power unless that person put it in. On my 356 carver you need to disconnect your shore cable before you run you gen. It is in the owners manual, once you start the gen the gen take over all electric. If you are hook up to your shore power and run your gen you have electric from both ends something is going to short out.
  12. NYCAP123

    NYCAP123 Senior Member

    Joined:
    Mar 14, 2008
    Messages:
    11,208
    Location:
    Long Island, NY
    :eek: Call me amazed that this is even permitted by NMMA specs or the CG. These should be called fireboats, as in yours will one day be on fire. Sounds like these boats were not made to have gens and whomever retrofitted didn't go the extra step.
  13. sam356

    sam356 Member

    Joined:
    Oct 31, 2011
    Messages:
    125
    Location:
    Great Oaks Fairlee Creek MD
    I think it is a bad idea but why would you run your gen at the dock. If I have shore power to it I do not need to run gen.
  14. sam356

    sam356 Member

    Joined:
    Oct 31, 2011
    Messages:
    125
    Location:
    Great Oaks Fairlee Creek MD
    NY cap sounds like you hope my family and me burn up in the boat you must make a great captain . I did not design the boat I like cavers that is why I have one. Thank you for hoping my family and I burn up.
  15. RB480

    RB480 Senior Member

    Joined:
    Feb 8, 2011
    Messages:
    226
    Location:
    New Buffalo, MI
    There is actually an automatic switch that is pretty common in boats. On mine you can actually hear it switch over when the generator is started just like if you were to flip the switch manually.
  16. NYCAP123

    NYCAP123 Senior Member

    Joined:
    Mar 14, 2008
    Messages:
    11,208
    Location:
    Long Island, NY
    God NO! It sounds like whomever designed that system is the one who didn't care. I've dedicated my life to keeping boaters safe. Systems like this are supposed to be idiot-proof. That's why most installations require you to block one side or rotate a switch so it's not possible to get juice from both the shore and the gen. One thing I've learned over a long life and especially a long life on the water is that the moment you assume nobody would ever do something, they'll do it. You should do what the original installer failed to do, and install a swith-over or even a slide bar at the panel that prevents the possibility of merging both sources. Even if you know better, a friend could decide to "help" you or even the next owner.
    A prime example of how disaster could strike is you're at a marina when the power goes out. So you fire up the gen. Then the power comes back on. My bud works for the power company and that's his biggest fear when doing storm restoration.